f1geek said:
Not a good idea to pull 30 amps on a 30 amp circuit. Trying to burn down the house? You probably should consult a licensed electrician. To my knowledge, you should not pull more than 80% of the circuit rating. If you only have a 30 amps circuit, don't pull more than 24 amps. If you can set the EVSE to 24 amps, that's what you should do. Otherwise, install an EVSE rated at 24 amps.
I doubt the house would burn down - more likely the breaker would trip, maybe after a delay. You may well be right in saying no more than 80% should be drawn (on a continuous basis I would suppose) so there is some allowance for start-up surge current (if that applies to these EVSE devices). I note that the advertised 30A units call for a 40A circuit.
Would still like to know however if the 30Aers can be adjusted lower (to maybe 24A as you suggest). In any case, looks like a 220V, 20A unit would be maybe 3 times faster than a L1(?).
Edit: Just noticed that 24A units are available so that looks like the way to go alright.